Just a note here- rather than using the record lows, you can go back to 
the future and use the ASHRAE minimum expected temperatures as the 2011 
NEC will allow explicitly. In the '08, it says to use the "lowest 
expected ambient temperature," for which the ASHRAE temperatures are 
more appropriate than record lows. These ASHRAE temps will be higher 
than the record lows and will add a little more cushion there at 600 VDC.

So where to get these temperatures? Starting on page 47:
http://www.solarabcs.org/permitting/Expermitprocess.pdf

Also, in case you didn't know, www.pvselect.com is another option for 
string sizing that features multiple inverters and a 1 degree 
temperature step rather than the 9 degree (F) temperature step on the 
SMA sizer. They have the Kyocera KD130 in their database, but not the KC130.

DKC

-------- Original Message --------
Subject: Re: [RE-wrenches] SWR2500U Inverter
From: Brian Teitelbaum <bteitelbaum at aeesolar.com>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Date: 2009/11/18 01:34

> Joel,
>  
> The SMA SWR2500U inverter has been a long discontinued model. If you 
> want to use an SMA inverter, go to the SMA website to use their 
> excellent sizing program. Plug in the module, and your record minimum 
> and average maximum temps for the site, and look for a current model 
> inverter that will work. All of the "U" series inverters (except for the 
> 700U) are discontinued models, and the "US" series are the current models.
>  
> If your min temp is not below 14⁰F, it looks like you can use all 24 in 
> one series string with the 4000US inverter, but that gets you awfully 
> close to 600VDC (595VDC) at 14⁰F. You might want to play it safe and 
> drop one of the modules. Unfortunately, none of the SMA inverters will 
> operate with only 12 modules in a string (with two strings). However, a 
> Fronius IG-3000 will, so you might want to go with that, although it has 
> a lower efficiency.
>  
> Brian Teitelbaum
> AEE Solar
>  
>  
>  
> -----Original Message-----
> From: re-wrenches-bounces at lists.re-wrenches.org 
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Joel 
> Davidson
> Sent: Tuesday, November 17, 2009 4:56 PM
> To: RE-wrenches
> Subject: [RE-wrenches] SWR2500U Inverter
>  
> Wrenches,
>  
> Our customer has 24 each Kyocera KC130 modules and wants to go grid-tied.
> Can he use an SMA SWR2500U inverter with the fan kit? Is there a better
> inverter that will use all of his modules? If you have an SWR2500U or a
> better inverter option for sale, please contact me off-list. Thank you very
> much.
>  
> Joel Davidson
>  
> _______________________________________________
> List sponsored by Home Power magazine
>  
> List Address: RE-wrenches at lists.re-wrenches.org
>  
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>  
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>  
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>  
> Check out participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>  
>  
> 
> 
> ------------------------------------------------------------------------
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 



More information about the RE-wrenches mailing list