What economical splice hardware are people using when you don't have two end of a ground wires to land in the Buchanan Splice Caps? Split bolts are mighty expensive....

-Chris Anderson
  Chief Technology Officer
  Resources Group 
  C: 603-732-2411
  Borrego Solar Systems

-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Peter Parrish
Sent: Tuesday, November 17, 2009 4:04 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Splice Caps

We have been using Buchanan brand "splice caps" to splice two to three #10
Cu EGCs inside 3R-rated j-boxes. Is there an approved methodology for
splicing ECGs under PV modules (i.e. exposed to the elements). I understand
that otherwise listed lay-in lugs are not acceptable for double lugging. -
Peter  

                                                     
Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parrish at calsolareng.com  
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885

 

-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dave Click
Sent: Tuesday, November 17, 2009 12:14 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Bonding Rails

Peter,

(1) it appears that per the WEEB installation manual:
http://www.we-llc.com/Datasheets/104-0404-000008-008.pdf
(page 8) you need to have one WEEB per module rather than one for every 
other module as you suggest.

(2) 690.43 Equipment Grounding.
Exposed non-current-carrying metal parts of module frames, equipment, 
and conductor enclosures shall be grounded in accordance with 250.134 or 
250.136(A) regardless of voltage.

I guess the latter answer depends on whether your AHJ considers the 
rails "exposed"-- I would, so in this situation I'd have lugs on each 
module and each rail.

DKC

-------- Original Message --------
Subject: [RE-wrenches] Bonding Rails
From: Peter Parrish <peter.parrish at calsolareng.com>
To: 'RE-wrenches' <re-wrenches at lists.re-wrenches.org>
Date: 2009/11/17 14:56

> We have been using WEEB clips on all of our installations for over a 
> year now. We include the WEEB data/installation sheets in our permit 
> package and patiently point out the clips to inspectors who haven't seen 
> the WEEB system yet.
> 
>  
> 
> Two questions:
> 
>  
> 
> (1)     For ProSolar rails, can we use one WEEB clip to bond two 
> adjacent modules (say, modules A and B) on the upper rail (say, rail #1) 
> and then use a second WEEB clip to bond the next two adjacent modules 
> (say, modules C and D) on the lower rail (say, rail #2) and then use a 
> listed lay-in lug (with in our case a WEEB clip) to bond to either rail 
> #1 or #2 to continue the grounding?
> 
> (2)     If we DON"T use WEEB clips and use the conventional bonding 
> methodology per module manufacturer's instructions (proper location on 
> the module, and listed screws, washers and nuts), do we have to ALSO 
> bond the rails? We have an inspector in Pasadena, CA that is requiring 
> this, but this is the first time we have been required to do so. Perhaps 
> in the past year in ignorant bliss we have missed an important 
> development? Or have we been dodging bullets for seven years and not 
> even knowing it?
> 
>  
> 
> - Peter
> 
> Peter T. Parrish, Ph.D., President
> California Solar Engineering, Inc.
> 820 Cynthia Ave., Los Angeles, CA 90065
> CA Lic. 854779, NABCEP Cert. 031806-26
> peter.parrish at calsolareng.com <mailto:peter.parrish at calsolareng.com> 
> Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885     
>

> 
>  
> 
>  
> 
> 
> ------------------------------------------------------------------------
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




More information about the RE-wrenches mailing list