Nik, we always use 4x4 gutters when ever possible - keeps things clean and neat - as long as insulation voltage rating is same on all wires and wires are bundled (AC and DC - tie wraps or tape) and it's all from the same system (house wiring is another system) then it's OK.......

Max Balchowsky 
SEE Systems




________________________________
From: "Nicholas Ponzio, Building Energy" <nponzio at buildingenergyus.com>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Thursday, September 24, 2009 4:02:21 AM
Subject: [RE-wrenches] AC & DC in Raceway

Wrenchers,

What's the deal with mixing AC and DC conductors in a raceway? The job in question has a 6x6 wireway under the inverters. Conductors will have their own conduits but is it ok for them to share the wireway?

Thanks in advance for clarification on this,