[RE-wrenches] Design help for solar water pumping application
Mark Dickson
mark at OasisMontana.com
Thu Jun 11 21:40:19 PDT 2009
Hey Lee,
Allan is right in that the WINcaps software is a lifesaver and FREE! Not to
contradict Allan, but I do not see a feasible way of using two float
switches in separate tanks with only one pump controller. Also, the 3000'
distance is a little far-they usually recommend a max distance of 1600' for
the float switches. Lastly, if you are ever worried about the head, the
Lorentz pumps can pump up to 760' --more than double the recommended for
Grundfos.
I highly recommend Genpro Energy Solutions as a pump distributor for both of
those brands. They always answer the phone, are personable and return
emails (hint, hint Conergy)!
Best,
Mark Dickson
Oasis Montana Inc.
<http://www.oasismontana.com/> <http://www.oasismontana.com/>
www.oasismontana.com
www.grid-tie.com <http://www.grid-tie.com/>
<http://www.pvsolarpumps.com/> <http://www.pvsolarpumps.com/>
www.PVsolarpumps.com
_____
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Thursday, June 11, 2009 2:28 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Design help for solar water pumping application
Lee,
You can get Grundfos' WINCaps software from your RE or pump supplier; some
will run the sizing for you (Jeremy at Conergy does for us). I didn't check
your head and flow, but I would expect that's about your only good pump
choice at that head. Add a tracker if you need greater summer output; don't
attempt batteries as a solution. If usage occasionally exceeds output, add
an IO101 control and allow the pump to run off any AC source at night. A
tiny 1,200W inverter/generator will work at sea level. Use a CU200
controller to allow a float or level detector switch to turn off the pump
when tanks are full. Mercury-based float switches last longer in signal
circuits that carry no current. If you can't use a float switch because the
lines are already buried, look into www.P2Flow.com <http://www.p2flow.com/>
for pressure transducer-based control. Read the website info, then call
Britt there with your specific application. That array sounds oversized, as
the pump draws a maximum of 900 watts. Hope this helps.
Allan Sindelar
<mailto:Allan at positiveenergysolar.com> Allan at positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
<http://www.positiveenergysolar.com> www.positiveenergysolar.com
_____
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Lee Bristol
Sent: Thursday, June 11, 2009 1:26 PM
To: RE-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] Design help for solar water pumping application
Solar Water Pumping Wrenches,
We normally don't do solar water pumping but a friend asked for some help
designing his system. He has one well and two 5,000 gallon reservoirs to
fill up. The average usage is expected to be about 2,000 gallons per day
but may be higher in the summer. The tanks will have level detector
switches to sense when the tank is full. The site is near Leesburg, VA.
The problem is to design a control system to turn on the pump when one or
both of the tanks needs water and to shut it off when both are full. The
closest tank has a head requirement of 200 feet (pump to tank) and is 300
feet from the well head. The second tank head requirement is 220 feet and
it is 3,000 feet from the well. The pipes are expected to be 1.25 or 1.5
inch.
A Grundfos SQFlex 6 SQF-2 pump with 1.36 KW solar was recommended, 360 foot
head, 360 gph. I think that this would provide the lift but not the
quantity. Hmmmm, what valves and controls would you all suggest?
Thanks!
Lee
--
Lee Bristol
NABCEP Certified Solar Designer/Installer
Chief Technology Officer
Standard Solar, Inc.
202 Perry Parkway, #7
Gaithersburg, MD 20877
(301) 944-5105
(240) 479-1510 (c)
www.standardsolar.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20090611/8525b4a4/attachment-0003.html>
More information about the RE-wrenches
mailing list