[RE-wrenches] Solar vent for flat roof
Allan Sindelar
allan at positiveenergysolar.com
Wed Apr 8 09:40:49 PDT 2009
We have twice used pairs of Zephyr Power Vents to successfully vent large
banks, up to around 2200A/hr @48V. A 12V unit exits roof or wall with a 2"
pvc stack; 48V is 3"; thus they flash just like standard plumbing vents.
Note that the charge rate is more important than battery capacity, as it
determines the amount of gassing that must be exhausted.
Allan at Positive Energy
-----Original Message-----
Wrenches,
Our client has 48 IBE 85N-15 batteries in a room with a flat roof. What is
your recommendation for a solar powered vent that works well and flashes
well so that it does not leak? Thanks in advance for your advice.
Joel Davidson