That looks like a great installation.  Is the max that can be fed 
into a generator mini grid 15%?

Since the system was able to keep the UL 1741 settings, that means 
this setup could feed both a utility grid and a generator mini grid, 
using the system transfer switch.

At 11:34 AM 3/13/2009, you wrote:

>We did a test installation in northern British Columbia with 28kW of 
>PV and GT5 inverters selling to a 90kW Genny system in a remote 
>off-grid community. So far we have just stuck to the normal 1741 
>islanding settings, and the system has been working smoothly. The PV 
>was basically sized so that it would not exceed the lowest mid-day 
>load on the small grid, and there was already an automatic dump load 
>in the system to ensure the diesels never became completely unloaded.
>
>
>
>So far the system has been working very well, with good fuel saving 
>for the community. You can read more about it here.
>
>