Aloha Solar Bozos:
    I haven't posted here in ages, and I hope I am cutting out the appropriate stuff?  Probably not, but I will give it a try.  I want to reply to Topic 3 regarding backfeeding an off-grid inverter with a grid-tied inverter.
    In 2004, I back-fed a SWR-2500U into an Outback FX inverter's back-up power panel.  It required a transformer to step down to 120VAC and a voltage controlled relay to shut the Sunny Boy off when the batteries were charged.  Greg at OB said that the inverters would regulate the AC output voltage at ~120V, so when the voltage would rise up from the Sunny Boy's production, the FX was forced to take the power in, resulting in the batteries being charged.  You probably realize that the Sunny Island controls the grid-tied inverter's output but fluctuating the Hertz, which eliminated that issue for them.


________________________________
From: "re-wrenches-request at lists.re-wrenches.org" <re-wrenches-request at lists.re-wrenches.org>
To: re-wrenches at lists.re-wrenches.org
Sent: Monday, August 3, 2009 6:47:22 AM
Subject: RE-wrenches Digest, Vol 2, Issue 818

Send RE-wrenches mailing list submissions to
    re-wrenches at lists.re-wrenches.org

To subscribe or unsubscribe via the World Wide Web, visit
    http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
or, via email, send a message with subject or body 'help' to
    re-wrenches-request at lists.re-wrenches.org

You can reach the person managing the list at
    re-wrenches-owner at lists.re-wrenches.org

When replying, please edit your Subject line so it is more specific
than "Re: Contents of RE-wrenches digest..."


When responding to posts within the Digest, be sure to restore the Subject: line to the original, and please edit out any extraneous lines from the quoted message.


Today's Topics:

   1. Re: AC Backfeed Battery Over-Charging (Jeff Yago)
   2. Broken Modules (Doug Wells)
   3. Re: AC Backfeed Battery Over-Charging (Tump)
   4. Re: Broken Modules (Jeff Yago)


----------------------------------------------------------------------

Message: 1
Date: Mon, 3 Aug 2009 06:21:56 -0700
From: "Jeff Yago" <jryago at netscape.com>
Subject: Re: [RE-wrenches] AC Backfeed Battery Over-Charging
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Message-ID: <20090803062156.CD9B16AE at resin17.mta.everyone.net>
Content-Type: text/plain; charset="us-ascii"

An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20090803/af3227a5/attachment-0001.htm>

------------------------------

Message: 2
Date: Mon, 3 Aug 2009 09:32:08 -0400
From: Doug Wells <dwells at thesolarspecialists.com>
Subject: [RE-wrenches] Broken Modules
To: RE-wrenches at lists.re-wrenches.org
Message-ID:
    <D6573665-38CE-4E54-A70F-F7AC8F630DF3 at thesolarspecialists.com>
Content-Type: text/plain; charset=US-ASCII; format=flowed

Wrenches,

I am curious what other installers are doing with broken modules?
I know some manufacturers are starting recycling programs.


Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com







------------------------------

Message: 3
Date: Mon, 3 Aug 2009 09:39:21 -0400
From: "Tump" <tump at hughes.net>
Subject: Re: [RE-wrenches] AC Backfeed Battery Over-Charging
To: <jryago at netscape.com>, "'RE-wrenches'"
    <re-wrenches at lists.re-wrenches.org>
Message-ID: <CAFB0B2FF97B4386BB4EF00DF46766F9 at tumpdggfbh2yn6>
Content-Type: text/plain; charset="us-ascii"

Hey Jeff this was something that Greg @ OB was working on summer of 06.....
Should have it tump, almost got it little problem .... Ahhh sorry we are no
longer working on that! I was in the middle of a large AC Coupled system &
had been waiting for 4 months for this "trick" soft ware to come on line.
Perhaps CF might be able to update us on this software. Kinda of a no
brainier perhaps, John B & the boys @ SMA patented this "trick" software.


     <mailto:Tump at swnl.net> Tump at swnl.net         <http://www.swnl.net/>
www.SWNL.net
           Solarwinds Northernlights  
   Serving Mid Coast Maine & Northern California
     Me.# 207-832-7574  Cl.#  610-517-8401

                          Blair "TUMP" May
      ********  MAINE'S CHARTER ********
            NABCEP    "Certified PV Installer" 
  
      ********  MAINE'S CHARTER ********
   Trace Xantrex "Certified" Dealer / Installer"
  
  

-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jeff Yago
Sent: Monday, August 03, 2009 9:22 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC Backfeed Battery Over-Charging


I have a question that may be one of those that everyone wants to know the
answer but feel they are the only one that doesn't know the answer, or
perhaps I am the only one that doesn't know!.  

In an AC-coupled system, i.e. the 240 VAC output solar inverter mounted at a
distant array (240 VAC out to reduce long line loss) is wired to the 120/240
VAC output emergency panel supplied from a battery based inverter.  This
allows the solar inverter to stay up when the grid goes down since it thinks
the grid is still up on the load side of the battery based inverter.  The
battery based inverter will use any excess backfed power from the solar
inverter that is in excess of the other supplied loads to re-charge the
battery.  However, when this happens the battery charging process can boil
the batteries when there are no other loads running.  

I have been told this is because the battery based inverter does not
regulate its charging of the battery when using backfed power from its
output panel, but I still don't understand why.  If the battery charger in
the inverter can provide regulated 3-stage battery charging when the power
is supplied from the grid or a generator, why does it suddenly become a full
output un-regulated battery charger when power is supplied from backfeed and
will keep charging regardless of reaching a high battery voltage?    

I would have assumed the battery charger section would charge the same way
regardless of where the power is being supplied from, or perhaps just
shutdown on some kind of backfeed safety.   As far as I know, this
over-charging problem in an AC coupled dual inverter system is true for all
battery-based inverters.   Any inverter techs out there that can explain
why?   Perhaps this would be a nice feature in future high-end battery-based
inverters so we no longer need the custom power relay field wiring to
provide this high voltage cut-out?.

Thanks,

Jeff Yago



  _____  

Netscape.  Just the Net You Need.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20090803/040f6858/attachment-0001.htm>

------------------------------

Message: 4
Date: Mon, 3 Aug 2009 06:47:21 -0700
From: "Jeff Yago" <jryago at netscape.com>
Subject: Re: [RE-wrenches] Broken Modules
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Message-ID: <20090803064721.CD9B1303 at resin17.mta.everyone.net>
Content-Type: text/plain; charset="UTF-8"

We have only had one broken module due to shipping damage and this was the bottom 200 watt module in a shipment where each 2 modules on the pallet were in heavy cardboard shipping boxes.  Of course this not discovered for several weeks until we worked our way down the stack.  However, since suppliers like Evergreen have switched to the plasic corners that allow stacking modules without any cardboard packaging, we have had no more breakage in shipment.  I assume the fork truck drivers now see a large stack of glass and take a little more care whenre thay ram the forks. 

As far as what we did with our broken module (which taught a very expensive lesson about checking shipments), we keep it to show students in our training classes what happens when things go wrong.

Jeff Yago

_____________________________________________________________
Netscape.  Just the Net You Need.


------------------------------

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



End of RE-wrenches Digest, Vol 2, Issue 818
*******************************************



      
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20090803/39b6e8ad/attachment-0002.html>


More information about the RE-wrenches mailing list