[RE-wrenches] Point of connection

Keith Cronin electrichi01 at yahoo.com
Mon Feb 9 14:40:59 PST 2009


Hello

With the growth of the solar industry coupled with the generous incentives now offered on fed part of the equation, we are seeing some trends here and wondering what the approach has been in other areas. What kind of feedback are you receiving from the AHJ?

There are some integrators who now are installing "systems" meaning, multiple small inverters that are married to smaller arrays as opposed to one large array with one large inverter. 

So, it is quite conceivable to have, for example, 3- 3000 W SMA inverters on a customers home. So, the point of connection issues arise. When you look at 690.64B, it speaks to the 120% of the busbar rating.

What are folks doing in other areas, for this above example to address the mechanical/electrical challenges associated with this situation, when if you had 1- 200 amp residential service? There is alot of discussion, like installing a 125 amp rated subpanel; interuppting the feeder from the electric service and installing a 225 amp panel with a higher rated buss (hard to find or custom made thru Cutler Hammer or others) etc.

We can also see a trend using the enphase products as well, but not as much pronounced. It could be conceivable for a client to want to build their system up over a few years and have 15, 175 watt panels on a circuit (2P15 amp) and grow the system up to lets say, 45, 175 watt panels (3-2P15 amp). Same situation, different inverter manufacturer. My sense is this trend will continue for the forseeable future, and alot of wrenches will find orphaned systems out there and we should look at ways to address point of connection issues that are bound to present themselves.

Thanks

Keith



      
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20090209/8a0ccc77/attachment-0002.html>


More information about the RE-wrenches mailing list