[RE-wrenches] Outback GTFX errors

Christopher Freitas cfreitas at outbackpower.com
Thu Apr 9 22:25:51 PDT 2009


The MATE is not responsible for the measurement - it simply shows the measurement and errors that the inverter reports. So I don't see how it could be the cause of your problem. 

There are a number of things to check on this - such as what the AC volt meter of the inverter says versus a good handheld volt meter - especially while the inverter is selling. If the AC wire is small or to long then there can be excessive voltage rise when the inverter is selling - but not while in the five minute delay period. 

Where you seeing the inverter cycle? Start selling and then stop in a minute or so? That's usually the problem caused by this sutuation. 

Contact me off-list and I will give you a couple other things to check and try. 

Christopher Freitas
OutBack Power Systems. 








Christopher

MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic Communication Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be protected by attorney-client or other privilege. If you believe that it has been sent to you in error, please do not read it. If you are not the intended recipient,you are hereby notified that any retention, dissemination, distribution, or copying of this communication is strictly prohibited.  Please reply to the sender that you have received the message in error, then delete it. Thank you.