[RE-wrenches] Dual XW glitches
    Mark Edmunds 
    mark.edmunds at xantrex.com
       
    Mon Dec 22 09:50:17 PST 2008
    
    
  
Hi William -
Might try running the inverter in question on its own, (set it back to
split-phase master) and see if it charges OK then. Also worth first
monitoring that inverter on the SCP (set the SCP to the home screen of
the affected inverter) and see what its "status" is when trying to
charge.
Once you have that data a call to the tech support line can get some
more pointers.
Cheers,
Mark
Mark Edmunds
Xantrex Technology Inc.
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Saturday, December 20, 2008 10:15 AM
To: RE-wrenches
Subject: [RE-wrenches] Dual XW glitches
Friends:
We have installed a number of single XW installations but only one dual 
XW.  The dual system is giving us some problems.  When the generator is 
started, both inverters will charge, but aft a minute or so, the slave
will 
stop charging.  This is even with very low batteries where both
inverters 
charging capabilities are needed.  Once I observed Inverter 2 trying
three 
times to charge but eventually giving up.
Has anyone experienced this?
Thanks for your input.
William
    
    