The formulas I learned in school are:
Single-Phase Vd = (2 * d * k * I) / cm
where: d = distance; the constant k = 12.9 Ohms for Cu & 21.2 Ohms for AL; I
= current; cm = circular mils
3-Phase Vd = (1.73 * d * k * I) / cm
My note are failing me, but I believe d is actually the one-way distance.
This is multiplied by 2, in the single-phase calculation, to account for the
round trip distance. In the 3-phase calculation 1.73 is used instead. Table
8 in the NEC has the conductor properties. This is where I always look up
circular mils.
In the past I¹ve run these calculations against my ElectriCalc & had things
check out.
>