Round trip...
 
(unless you are using a table that has already counted this in)
 
Take care,
Walt
 
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Marco
Sent: Monday, December 08, 2008 2:13 PM
To: re-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] voltag drop
 
I feel kinda foolish in asking this.....but when calculating voltage drop in
a conductor over distance, do I use the one-way or round-trip distance?
 
thanks,
marco
 