[RE-wrenches] grid-tie inverters & generators
Drake Chamberlin
drake.chamberlin at redwoodalliance.org
Thu Nov 20 07:41:12 PST 2008
Talking to SMA, during a 4248 Sunny Island installation, w/ AC
coupled Sunny Boys and a generator backup via transfer switch, I was
told that backfeed to the generator needed to be addressed. The
Sunny Island has a setting that will limit backfeed to the generator
to a value that can be set by the installer. The setup requires that
a relay in the transfer switch or generator close when the generator
is on, to send a signal to the Island. I was told that backfeed had
to be set to less than 100 watts.
SMA tech support also reported that a number of generator control
boards have been fried by inverters back feeding generators.
Drake
At 08:28 PM 11/19/2008, you wrote:
>In a message dated 11/19/2008 5:25:30 PM Pacific Standard Time,
>kelly at whidbeysunwind.com writes:
>I can imagine, if the inverter tries to sync with the inverter, that
>the voltage could rise, causing the inverter to disconnect, wait 5
>minutes, repeat. Is there anything nasty that could happen?
>
>
>
>Kelly, That is the way I see it. I have tested systems with gens and
>had no issues. The Sunny Boy would not boot to a gen
>source. However, you can understand what the official position must
>be. There exist gensets with accuracy or it might just happen by
>chance. Low probability, but not zero.
>
>Don Loweburg
>
>
>
>
>----------
>One site has it all. Your email accounts, your social networks, and
>the things you love. Try the new
><http://pr.atwola.com/promoclk/100000075x1212962939x1200825291/aol?redir=http://www.aol.com/?optin=new-dp%26icid=aolcom40vanity%26ncid=emlcntaolcom00000001>AOL.com
>today!
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
740-448-7328
740-856-9648
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20081120/dd86b1e5/attachment-0004.html>
More information about the RE-wrenches
mailing list