Hi Folks,
We burnt up a gen set's voltage regulator on an off-grid system sunny
island/sunny boy system when we took the sunny island's off-line but
didn't shut off the sunny boy. So the SB backfed the genny and fried
the very expensive voltage regulator on a 30 KW system. SMA had us
install a relay to tell the SB to shut down as soon as the AC
reference from the SI was gone. Same situation as grid-tie really in
terms of your question.
Jeff
>Hi Kelly
>
>It is an interesting issue and was just dicussing this the other day.
>
>I think what happens if the inverter backfeeds the genny, the
>generator voltage will go up, if it goes up enough, it will go
>outside the window of the inverter and the inverter will drop out,
>voltage will them return to normal, inverter will reconnect and
>repeat.
>
>But I sure wouldn't want to fix the generator. A relay powered from
>the grid will take care of the problem.
>
>jay
>
>peltz power
>On Nov 19, 2008, at 5:24 PM, Kelly Keilwitz, Whidbey Sun & Wind wrote:
>
>>Wrenches,
>>I'm dredging up this subject again (previous postings 6/08) with a
>>simple question that doesn't seem to have been answered:
>>
>>Is there any issue connecting a batteryless grid-tie PV system to
>>the load side of a panel that is backed-up by a generator on an
>>automatic transfer switch, when the grid is down and the generator
>>running?
>>
>>In this case the PV is 5.7kW, the inverter an SMA 6000, the
>>generator unknown size/type, but propane, automatic start, and
>>backing up the entire main panel.
>>
>>SMA tech support first said it's OK, then that the generator will
>>blow up. I can imagine, if the inverter tries to sync with the
>>inverter, that the voltage could rise, causing the inverter to
>>disconnect, wait 5 minutes, repeat. Is there anything nasty that
>>could happen?
>>
>>Thanks,
>>-Kelly
>>
>>
>>Kelly Keilwitz, P.E.
>>Whidbey Sun & Wind, LLC
>>Renewable Energy Systems
>>NABCEP Certified PV Installer
>>987 Wanamaker Rd,
>>Coupeville, WA 98239
>>PH & FAX 360-678-7131
>><>sunwind at whidbeysunwind.com
>>
>>
>>
>>
>>
>>_______________________________________________
>>List sponsored by Home Power magazine
>>
>>List Address:
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Options & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive:
>>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>List rules & etiquette:
>>www.re-wrenches.org/etiquette.htm
>>
>>Check out participant bios:
>>www.members.re-wrenches.org
>>
>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
--
~~~~~~~~~~~~~
Jeff Clearwater
Senior Design Engineer
NABCEP (tm) Certified Solar PV Installer
http://www.nabcep.org/
Village Power Design/NorthEast Solar Design
Turnkey Solar Design & Installation for the Commercial Sector
http://www.villagepower.com
gosolar at villagepower.com
Voice: 413-259-3750
Fax: 413-825-0703
65 Schoolhouse Rd
Amherst, MA 01002
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20081120/37b612c2/attachment-0004.html>
More information about the RE-wrenches
mailing list