[RE-wrenches] grid-tie inverters & generators

Drake Chamberlin drake.chamberlin at redwoodalliance.org
Wed Nov 19 20:52:21 PST 2008


At 06:24 PM 11/19/2008, you wrote:
>Is there any issue connecting a batteryless grid-tie PV system to 
>the load side of a panel that is backed-up by a generator on an 
>automatic transfer switch, when the grid is down and the generator running?


It is recommended to use a relay to disconnect the inverter when the 
panel is being fed by the generator.


Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
740-448-7328
740-856-9648  





More information about the RE-wrenches mailing list