[RE-wrenches] grid-tie inverters & generators
    Drake Chamberlin 
    drake.chamberlin at redwoodalliance.org
       
    Wed Nov 19 20:52:21 PST 2008
    
    
  
At 06:24 PM 11/19/2008, you wrote:
>Is there any issue connecting a batteryless grid-tie PV system to 
>the load side of a panel that is backed-up by a generator on an 
>automatic transfer switch, when the grid is down and the generator running?
It is recommended to use a relay to disconnect the inverter when the 
panel is being fed by the generator.