[RE-wrenches] Pt valves as overheat control
Glenn Burt
glenn.burt at glbcc.com
Wed Nov 12 15:12:36 PST 2008
Radiantec makes a heat dump valve that activates at a temp you set via a
controller that may be a safer way to divert over heated water...
http://www.radiantec.com/pdf/End_Uses_of_the_Solar_Energy.pdf
pp4
-Glenn Burt
_____
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Roy Butler
Sent: Tuesday, November 11, 2008 11:15 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Pt valves as overheat control
Hi guys,
I have been using the SS water loop in my Amish wood cookstove
for my domestic hot water for 9 years now. My tank is a 40 gallon
electric water heater (space saver unit) and is configured for thermo
siphon operation.
The P/T valve is all I have for protection and I have to be honest,
I kind of knew this was probably not a great idea right from the start!
But it works....the valve opens up and discharges into a piping system
located under a raised bed planting area in our attached green house.
So we get the benefit of the 'waste' heat. The valve opens, on average,
about 1 or 2 times a week during the coldest part of the winter.
I replace the P/T valve every other heating season because it does
begin to weep a bit. So that may be what's saved my ignorant butt
from being blown to bits.....maybe.
My question....is there a more robust version of that P/T valve
that I should be using? Something that you would use in a boiler perhaps?
I'm hoping to not have to change the system too much....I love the
long, guilt free showers....more so because the electricity for the
pump comes from my off-grid hybrid system.
I'm so much better at PV and wind systems....hot water scares me!
Roy Butler
NABCEP Certified Solar PV InstallerR
NYSERDA eligible PV & wind installer
Four Winds Renewable Energy, LLC
8902 Route 46
Arkport, NY 14807
607-324-9747
www.four-winds-energy.com
www.nationalsolarsupply.com
Although no trees were killed in the sending of this message,
a large number of electrons were terribly inconvenienced.
Todd Cory wrote:
Sure, but the discussion was about preventing hot water storage tanks from
exploding. Putting BTUs into a tank, whether that be from a wood stove loop
or 5 kW electric heating element is not the issue. Relying on a P/T valve to
regulate overheating is of course not a good idea, but it will prevent the
tank from exploding.
Todd
Conrad Geyser wrote:
Todd,
I'm afraid that any PT valves that I've ever known have continued to weep
indefinitely after one or two overheat triggers.
I would not recommend relying on them for heat control devices.
Conrad
Cotuit Solar
NABCEP thermal cert.
<!--[endif]-->
_____
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20081112/7f603567/attachment-0004.html>
More information about the RE-wrenches
mailing list