My rusty memory was telling me the 4248 was listed by ETL.  From my
hotel room in sunny San Diego :-), a quick drill-down into ETL's Listed
Mark Directory found this:
Inverter Charge Controller, Model No. SI4248U.  Evaluated to the
following...A representative sample of the listed devices have been
tested, investigated and found to comply with the requirements of the
Standard(s) for Safety Inverters, Converters, & Controllers for Use in
Independent Power Systems (UL-1741) and are identified with the ETL
Listed Mark.
http://etlwhidirectory.etlsemko.com/WebClients/ITS/DLP/products.nsf/6a42
1efeead6f216852568d4005862af/8714764900c91ce78525737f0049ce6e?OpenDocume
nt&ExpandSection=2&Highlight=0,SMA#_Section2

Similar for Canada, but with the cETL:
http://etlwhidirectory.etlsemko.com/WebClients/ITS/DLP/products.nsf/6a42
1efeead6f216852568d4005862af/81e240dda7c6a59e8525737f0049bbff?OpenDocume
nt&ExpandSection=2&Highlight=0,SMA#_Section2

However, I would discuss (nicely) with the AHJ about the reasonableness
of their requirement to provide the manufacturer's original
certification -- after all, the inverter is either listed to UL1741 or
it isn't, and confirming this is a simple matter of looking for the
listing mark on the equipment installed.  An installer would have to be
pretty brave to try to sneak a non-listed inverter through.  Pretty soon
we'll have to do secret utility-interactive handshakes to prove our
worthiness. Although now that I think of it, that certainly would make
the floor show this week far more entertaining.....

More ocean! More sun!  


Phil Undercuffler
Director, Battery-based and Off-grid
Distribution Sales Group
Conergy 
Our World Is Full of Energy
1730 Camino Carlos Rey Suite 103
Santa Fe, NM  87507
p.undercuffler at conergy.us
Direct | 505.216.3841
Toll Free | 888.396.6611 x4841
Fax | 505.473.3830
www.conergy.us
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Glenn
Burt
Sent: Monday, October 13, 2008 11:13 AM
To: 'Michael Kelly'; 'RE-wrenches'
Subject: Re: [RE-wrenches] SMA Sunny Island

Mike,

Thanks for the reply,

Our utility (National Grid) however has recently started requiring a
copy of
the original certification issued to the manufacturer of the equipment,
so
this has been insufficient. As has the cut sheet which bears the ETL
stamp,
or the web page that said it was tested successfully. We have to submit
the
UL or other certification for each install we do in their territory at
this
time.

So I need a copy of the certificate issued to SMA for this product -
their
other certifications are listed on their website, but not this one.

-Glenn

-----Original Message-----
From: info.solarflair at gmail.com [mailto:info.solarflair at gmail.com] On
Behalf
Of Michael Kelly
Sent: Monday, October 13, 2008 12:15 PM
To: glenn.burt at glbcc.com; RE-wrenches
Subject: Re: [RE-wrenches] SMA Sunny Island

Glenn,

It meets UL 1741 based on the first paragraph on page 10 of the user
manual:

http://www.sma-america.com/en_US/products/off-grid-inverters/sunny-islan
d-42
48u/dl/U0k0MjQ4VV9NYW51YWw%3D/download.html

Best,
Mike

On Mon, Oct 13, 2008 at 11:26 AM, Glenn Burt <glenn.burt at glbcc.com>
wrote:
>
> Hello esteemed colleagues,
>
> Can anyone tell me for certain (as in they have seen a copy of it) if
the
> Sunny Island 4248 has been listed by UL or another NRTL? I can't seem
to
> find mention of it on the SMA website (although the SI-5048 is there),
or
> the UL list.
>
> Thanks for the help!
>
>
> Regards,
>
> Glenn Burt
> Technical Specialist
>
> Renewable Power Systems, LLC
> PO Box 967
> Averill Park, NY 12018
> V: 518-674-5808
> C: 518-810-3174
> F: 518-514-1175
> E: gburt at RPSPower.com
> www.RPSpower.com
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>



--
Michael Kelly
Project Engineer
Project Manager

SolarFlair Energy, Inc.
1 Knoll Rd.
Hopkinton, MA 01748
Direct Mobile: 617-899-9840
Direct Fax: 781-272-0748
Main Phone: 508-293-4293
Main Fax: 508-293-4003
mike at solarflair.com

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




More information about the RE-wrenches mailing list