[RE-wrenches] Low Voltage Disconnect
jay peltz
jay at asis.com
Tue Sep 23 09:53:53 PDT 2008
HI Allan and Walt,
I might suggest a Solid State relay instead of a standard unit.
This will work fine on the MX AUX relay, are totally sealed, and very
reliable.
The MX model line is no more, been replaced with the FM 60/80.
jay
Peltz Power
On Sep 22, 2008, at 8:39 AM, Allan Sindelar wrote:
> Walt,
> In my experience, relays are simple and reliable solutions,
> especially the 30A open-coil type. I would suggest the MX60's LVD
> auxiliary function to control a 12V DPST open-coil relay with a 12V
> coil (Grainger 5Z556). To add additional protection against long-
> term arcing causing contact pitting, series or parallel the contacts.
> What's an MS-60?
> Allan at Positive Energy
>
> -----Original Message-----
>
> Hello all,
>
> I have an application where a customer has a continuous 40watt load
> in a remote location (similar to telecom).
>
> We are looking at the MS-60 or MX product for charge control, but
> neither of these has a LVD without using additional relay equipment.
>
> The charging current coming in from the panels (if we are forced to
> stay with 12V) is right at 60 amps.
>
> To get the low voltage disconnect function, do you see any problem
> going with multiple PS-30M charge controllers, and using just one of
> them for the 40W load?
>
> Thanks,
>
> Walt
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20080923/8fb1cb90/attachment-0004.html>
More information about the RE-wrenches
mailing list