[RE-wrenches] battery reference gen start module
Walt Ratterman
wratterman at sunenergypower.com
Thu Aug 28 12:59:55 PDT 2008
Hello all,
In our installations in the developing world, we do not do auto start
(things just don't generally work automatically...), but we use the GenAlert
function to sound an alarm (telling the operator that the battery needs to
be charged.)
The alarm goes on at 47.2 VDC (48V system). We generally set it go off when
the charging has taken the battery up to its float voltage parameter, but
that does not mean that the generator goes off. (The audible portion of
the alarm can be silences via a timer switch for up to 6 hours..)
If the alarm is ignored, we have the LVD set at either 46 V or higher.
Walt Ratterman
SunEnergy Power International
www.sunepi.org
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Tump
Sent: Thursday, August 28, 2008 12:54 PM
To: re-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] battery reference gen start module
What are folks using to start generators using voltage parameters?
<mailto:Tump at hughes.net> Tump at hughes.net <http://www.swnl.net/>
www.SWNL.net
Solarwinds Northernlights
Serving Mid Coast Maine & Northern California
Me.# 207-832-7574 Cl.# 610-517-8401
******** MAINE'S CHARTER ********
NABCEP "Certified PV Installer"
******** MAINE'S CHARTER ********
Trace Xantrex "Certified" Dealer / Installer"
__________ Information from ESET NOD32 Antivirus, version of virus signature
database 3397 (20080828) __________
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20080828/edab3092/attachment-0004.html>
More information about the RE-wrenches
mailing list