[RE-wrenches] offgrid system question

robert ellison reellison at gmail.com
Mon Aug 18 13:41:06 PDT 2008


You don't list what the inverter is, but you might find that the battery
voltage is dropping like lead when when the AC starts.  If the system always
started he AC look to the batteries, not good choice IMHO
Another thing is, systems tend to grow with time and out grow the systems
intended loads.
How old is thw system?

Later,
Bob

On 8/18/08, Max Balchowsky <max at seesolar.com> wrote:
>
>
>
>  Dear wrenches, going to look at a system installed by others and would
> like some input from some of you with more off grid experience than I have (
> 4 systems over the years). the system was put on a new home - off grid 20
> sharp ND123UJF panels 4 modules in series - 5 parrallel strings, 2460 total
> array dc voltage. mppt 60-150 charge controller, 12 sun extender sealed AGM
> batteries, 305 AH at 12 vdc, wired for 915 AH at 48 volt DC. The system is
> tripping off when the AC unit trys to start - AC is comfortmaker 3.5 ton 13
> seer. They say start up inrush is 104 amps (sounds high to me) and they put
> a DST 10 soft start on the unit (I think that's just a big capacitor). I
> haven't been on site yet but it sounds to me that they just didn't design
> enough inverter capacity into the system...... What are your thoughts?
>
> Max Balchowsky
> SEE Systems
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> RE-wrenches at lists.re-wrenches.org
>
> http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20080818/694a2414/attachment-0004.html>


More information about the RE-wrenches mailing list