[RE-wrenches] Imbalanced Legs in 3-Phase systems
Darryl Thayer
daryl_solar at yahoo.com
Thu Aug 7 17:31:58 PDT 2008
I have heard the 6kW imbalance rule. However when I spoke with the area Engineer from the Utility, he said he would not be at all concerned with 10% imbalance. in fact unless I was to exceed 20% not to worry. The system was a 800 amp 480 volt. He of course said my concern is more where I feed the panel to connect. Which is the concern of the electrical inspector.
Darryl
--- On Thu, 8/7/08, Jeff Clearwater, Village Power Design <jeffc at villagepower.com> wrote:
> From: Jeff Clearwater, Village Power Design <jeffc at villagepower.com>
> Subject: [RE-wrenches] Imbalanced Legs in 3-Phase systems
> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> Date: Thursday, August 7, 2008, 12:13 PM
> Hi Wrenches,
>
> How does one determine how much imbalance can be tolerated
> on a 3 phase system?
>
> I'd like to feed 2 SMA SB5000s at 277 VAC into a 480
> VAC panel
> instead of 1 13 KW Solectria at 480VAC as the PV system is
> only 9500
> Watts STC. The main on the backfed service panel is 600 A.
> But I'm
> not that sure of the loads as it's new construction and
> hasn't been
> characterized.
>
> What are the appropriate calcs to do here?
>
> Thanks!
>
> Jeff C.
> --
> ~~~~~~~~~~~~~
> Jeff Clearwater
> Village Power Design
> Sustainable Energy & Water Solutions for Home &
> Village
> http://www.villagepower.com
> gosolar at villagepower.com
> NABCEP (tm) Certified Solar PV Installer
>
> Voice: 413-259-3776
> Fax: 413-825-0703
> 65 Schoolhouse Rd
> Amherst, MA 01002
> ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~`~
> _______________________________________________
> List sponsored by Home Power magazine
>
> RE-wrenches at lists.re-wrenches.org
>
> http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
More information about the RE-wrenches
mailing list