XW6048 running a 1HP pump? [RE-wrenches]

Mark Edmunds mark.edmunds at xantrex.com
Tue Jun 10 11:14:45 PDT 2008


Hi Scott,

With a good battery bank this should work. It's on the edge and the
voltage will sag during the surge but as long as the battery voltage
stays above the low voltage cut out point it should handle this start
up.

Cheers,

Mark


Mark Edmunds
Xantrex Technology Inc.

-----Original Message-----
From: Scott Carlson [mailto:scott at carlsonsolar.com] 
Sent: Tuesday, June 10, 2008 10:08 AM
To: RE-wrenches at topica.com
Subject: RE: XW6048 running a 1HP pump? [RE-wrenches]


Mark,
I have a customer that has a pump that supposedly takes 82.6 amps @240
to
start. Less than a second. Can the XW handle this? Seems to me the
breakers
will hold.