Phil,

            Not really a big fan of auto starting generator, especially when
no one is on-site. But for my remote clients that are not on site 24/7 I use
a two relay system with 12vdc coils. When the generator wants to start the
first relay starts the heater (big load) and also starts a time delay relay
with a setting of .1 to 60 minutes. After the timer times out the start
signal is given to start the generator. Feed back from generator installers
is they normally want 45 to 60 minutes of heat before starting the
generator. Keep in mind that you will want the start signal from the
inverter (normally based on voltage) to be a little higher than normal
because when you turn that block heater on it is going to use a ton of
power. Our temperatures up here in the Adirondacks’ can easily get into
-30F. Good luck.

 

Chris Schaefer

Solar and Wind FX Inc.

5115 South Hill Road

Canandaigua(Bristol Center) New York 14424

585.229.2083

Cell 748.1870

chris at solarandwindfx.com

HYPERLINK "http://www.solarandwindfx.com/"http://www.solarandwindfx.com/

Where Knowledge Equals Power Independence

 

 

***CONFIDENTIALITY NOTICE*** 

The information in this email may be confidential and/or privileged. This
email is intended to be reviewed by only the individual or organization
named above. If you are not the intended recipient or an authorized
representative of the intended recipient, you are hereby notified that any
review, dissemination or copying of this email and its attachments, if any,
or the information contained herein is prohibited. If you have received this
email in error, please immediately notify the sender by return email and
delete this message from your system.

 

 

 

Wrenches,

 

Do any of you cold-weather wrenchers have recommendations for a

propane-fired block heater for tough winter starting?  Maybe even relay

controlled to start heating in anticipation of an inverter-controlled auto

start?  Thanks.

 

cheers,

P.

 

Phil Schneider

Creative Energies

Lander, WY

 

 

- - - -

Hosted by Home Power magazine

 

To send a message: RE-wrenches at topica.com

 

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

 

List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php

 

Check out participant bios: www.mrsharkey.com/wrenches/

 

Moderator: michael.welch at homepower.com


 

 

 

No virus found in this incoming message.

Checked by AVG. 

Version: 7.5.524 / Virus Database: 269.23.7/1409 - Release Date: 01-May-08
08:39

 


No virus found in this outgoing message.
Checked by AVG. 
Version: 7.5.524 / Virus Database: 269.23.7/1409 - Release Date: 01-May-08
08:39
 

[Non-text portions of this message have been removed]


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------





More information about the RE-wrenches mailing list