If their minimum load is not at least 110% of the inverter nameplate rating, you will have difficulty. Even if that minimum demand is happening outside of the system's max output, you may end up talking to a brick wall.

David Buckner

 

-----Original Message-----
From: Steven Lawrence <stevel at thesolarcenter.com>
Sent: Wednesday, February 06, 2008 10:32 AM
To: RE-wrenches at topica.com <RE-wrenches at topica.com>
Subject: Con Ed's Reverse Power Device [RE-wrenches]


I'm in the process of applying for interconnectin on a 21kw system for a 
new building with a 1200A, 3phase 208 service.  Because New York doesn't 
require net metering on systems over 10kw, Con Edison is requiring a 
reverse power device (Con Ed Device 32R) that'll shut down the system if 
it ever starts to backfeed their grid.  I've already tried asking them 
to install a non-bidirectional meter with no luck.  I am in the process 
of getting the energy demand calculations to show that the peak system 
output will never match the loads of the building, but I don't know if 
that'll work given Con Ed's stubbornness on other systems we've 
installed.

Has anybody had any experience with this?  If so, have you managed to 
get them to drop this requirement?

Steven Lawrence
The Solar Center
NABCEP Certified Solar PV Installer™


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------





More information about the RE-wrenches mailing list