If you had, for instance, strings of quantity 10 PVL136 watt modules, and
you needed to put in a 68 watt module because of a skylight, then you would
want to use a string of 9 PVL136 watt + 2 PVL68 watt.  This would keep the
voltages the same between strings.  Having a string of 9 PVL136 + 1 PVL68
paralleled with strings of 10 PVL136 would cause some of the strings to see
non-optimal voltages.  I don't see how bypass diodes would fix things.


> Message: 1
> Date: Thu, 30 Oct 2008 13:29:38 -0700 (PDT)
> From: Geoff Greenfield <geoff at third-sun.com>
> Subject: [RE-wrenches] mix-n-match Unisolar
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Cc: Randy <Randy at third-sun.com>
> Message-ID:
>        <7296183.5724731225398578887.JavaMail.root at zimbra4.mindcentric.com>
> Content-Type: text/plain; charset="utf-8"
>
>
>
> I thought I knew the answer to this one, but wanted to run it by the list.
>
>
>
> We are responding to a bid where the electrical engineer has designed a
> system with different sized Uni-solar laminates in some?series strings
> paralelled with consistant full size strings.? (this was done to work around
> skylights etc).
>
>
>
> We suggested that this was a poor design and will lead to "least common
> denomenator" performance, exacerbated by MPPT confusion.? The EE responded
> that "the bypass diodes allow for this".
>
>
>
> Any experience with this in practice?
>
>
> For a brighter energy future,
>
> Geoff Greenfield
> Founder and CEO
> Third Sun Solar & Wind Power Ltd.
> 340 West State Street, Unit 25
> Athens, OH 45701
>
> 740.597.3111 ? ? Fax 740.597.1548
> www.Third-Sun.com
>
> Clean Energy - Expertly Installed
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20081030/05cea4f7/attachment-0003.html>


More information about the RE-wrenches mailing list