[RE-wrenches] Getting "GFDI Open" Message When It's Not

Kelly Keilwitz, Whidbey Sun & Wind kelly at whidbeysunwind.com
Mon Sep 22 21:37:13 PDT 2008


Hi All,
We¹ve seen this on 2 SMA SB¹s (one a 3000; can¹t recall the other) this
year. In both cases we got it to work by fiddling with the jumper. Another
installer recommended that trick.
-Kelly

Kelly Keilwitz, P.E.
Whidbey Sun & Wind, LLC
Renewable Energy Systems
NABCEP Certified PV Installer
987 Wanamaker Rd, 
Coupeville, WA 98239
PH & FAX 360-678-7131
sunwind at whidbeysunwind.com


On 9/22/08 4:08 AM, "design" <design at elementalenergy.com> wrote:

> I have also seen this GFDI OPEN message on a few SB3000US units.  I have
> managed to get the unit to boot properly by switching it off, pulling the GFDI
> fuse out, slightly crimping the fuse clips to make them tighter, then putting
> fuse back in and switching it on.  This may have actually had an affect, or it
> may have simply been the restart that did it.  In any case it seems like this
> may be a more common occurrence than SMA knows. Two units required one
> restart, one unit took three before it finally booted correctly.
> 
>  
> 
> Jim Grundy
> 
> NABCEP Certified Solar PV Installer
> 
> Vermont Solar Specialist Plumber PS-279
> 
> Elemental Energy, Inc.
> 
> 1750 Clark Rd
> 
> E. Montpelier, VT   05651
> 
> 802-476-3441 (p)
> 
> 802-476-5680 (f )
> 
> 802-272-8933 (c)
> 
> 
> 
> 
> 


 


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20080922/54d7f187/attachment-0003.html>


More information about the RE-wrenches mailing list