[RE-wrenches] offgrid system question
Phil Undercuffler
P.Undercuffler at conergy.us
Tue Aug 19 07:39:55 PDT 2008
The XW6048 is rated at 52 amps RMS line to line between 5 seconds down
to 1 millisecond, so if your client's AC has a starting inrush surge of
104 amps at 240v, then yep, I think your biggest problem is not enough
inverter. Sounds like just one additional inverter will be marginal;
depending upon the additional background loads you may want to consider
expanding to three total. I think Mick Abraham is right on here, in his
earlier post.
Phil Undercuffler
Director, Battery-based and Off-grid
Conergy Sales & Systems, Americas
Our World Is Full of Energy
1730 Camino Carlos Rey Suite 103
Santa Fe, NM 87507
p.undercuffler at conergy.us <mailto:p.undercuffler at conergy.us>
Direct | 505.216.3841
Toll Free | 888.396.6611 x4841
Fax | 505.473.3830
www.conergy.us <http://www.conergy.us/>
________________________________
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Max
Balchowsky
Sent: Tuesday, August 19, 2008 6:45 AM
To: mick at abrahamsolar.com; RE-wrenches
Subject: Re: [RE-wrenches] offgrid system question
You're right Mick, It is an XW 6048, there's only one and I really think
I'm going to find that the biggest problem is that there is not enough
inverter capacity capacity with just one unit (the scematic shows a 60
amp breaker on the output). The system is new ( installed within the
last 4 months and the batteries were new) The AC unit is 240 volt.....
Max Balchowsky
SEE Systems