HI Bob,

What are you using 80v battery banks for or which inverters anyway?

Would be great for larger systems.

thanks,
jay
peltz power


On Aug 1, 2008, at 10:18 PM, robert ellison wrote:

> When i went to an SEI class at the Trojan factory one of the points  
> mentioned was that the best way to get the lowest cost per watt  
> from the battery bank
> (T-105's were at the time the lowest) was to cycle them to 80%  
> discharge then fill them all the way up. Not feasible in an off  
> grid system at all.
> We get more years life by just taking off the top 20 - 25% and  
> returning it daily.
>
> My battery distributor says that an industrial deep cycle battery  
> needs to be cycled occasionaly to prevent them developing a  
> "memory" so to speak.
> I recommend to my customers that they occasionally let them run  
> down to 50 -60% DOD and fill them back up with an EQ charge to stir  
> up the electrolyte so you can get an accurate reading with a  
> hydrometer.
> Stratification will throw off the gravity readings unless they get  
> stirred up occasionally.
> I have pulled apart batteries that did not get an EQ and found the  
> bottom of the plates wore out and the top still looking reasonably  
> good. That is from the acid being a lot stronger at the bottom than  
> the top and just working on the bottom of the plates in the  
> battery. This is not a "fun" project and usually results in some  
> trashed clothes, rubber suit or not.
>
> I have 80 volt battery packs that get cycled to 70-80% DOD daily  
> for 5 months a year then sit for 7 months with just a couple  
> freshening charges and last 6 - 7 years till wore out, some of  
> these are hi acid batteries that are in the specific gravity range  
> or 1.325 or more when fully charged instead of the usual 1.265  
> -1.270 that we are used to seeing.
>
> I am not a battery "expert" I just have several big banks that I  
> maintain and have formed some opinions over the last 15 or so years.
> I have also experienced wearing out a set of L-16's by hitting the  
> end of their cycle life in just over a year. It was way too small a  
> battery bank and got cycled fully almost daily hitting it's cycle  
> life limit far sooner than a larger bank would have if treated well.
>
> Good night,
> Bob
>
>
>
>
>
> On Sat, Aug 2, 2008 at 12:01 AM, jay peltz <jay at asis.com> wrote:
> Hi Robert,
>
> When you mention cycling batteries, are you saying that batteries  
> in a offgrid system that are being cycled 15-25% a day should be  
> cycled even deeper than that?
>
> Thanks,
>
> jay
> peltz power
>
> On Aug 1, 2008, at 8:36 PM, robert ellison wrote:
>
>> A couple things that I haver noticed in the past, sometimes  
>> batteries like to be cycled, shut off the controllers and run them  
>> down, then charge them up fully and then give them an eq charge  
>> till it comes up the peak voltage and hold it there as it  
>> (sometimes) slowly rises. Any of these thoughts are superseded by  
>> Jamie if he has any thoughts.
>>
>> Also, if you have not given them an eq in a while it might take  
>> longer than the available solar time has to get them to the top  
>> and hold them there..
>> Have the controllers settings changed?
>>
>> Bob
>> On Fri, Aug 1, 2008 at 10:18 PM, Allan Sindelar  
>> <allan at positiveenergysolar.com> wrote:
>> Wrenches,
>> In late 2003 we installed a 24V set of Rolls-Surrette 4-KS-21PS 6V  
>> 1104 A/hr batteries in the off-grid system of a long-time client.  
>> The client's system had a democracy array of around 800 watts of  
>> tracked PV. In early 2005 we added 1,280 watts of additional PV,  
>> and the client hasn't run the generator since; the system rarely  
>> drops below 80% and fills to 100% most days in sunny New Mexico.  
>> Batteries are located in a basement, so temperatures stay  
>> relatively constant, although it will vary slightly seasonally.  
>> MX60 controller is temperature compensated, with 29.6 VDC bulk and  
>> 31.4 VDC EQ set points.
>>
>> The problem is that the client reports being unable to achieve  
>> previous EQ voltages, and this inability appears to be a new  
>> development. The system is otherwise performing well. As the  
>> client is sharp and pays close attention to the system's  
>> operation, I'm not ready to blame user ignorance (with one  
>> possible exception; read on). This may be an issue of seasonally  
>> warm temperatures, but I'm not sure this would explain the full  
>> 0.4 VDC reduction in voltage. I told him that I would post his  
>> problem to this list, and also request advice from Surrette Battery.
>>
>> Here is the client's description of the symptoms:
>> I'm concerned that I am unable to equalize batteries at this  
>> time.  Up
>> until June of this year the Tri-Metric readings during equalizing  
>> indicated
>> holding voltage at 31.1, with maximum amps gain of around 52.    
>> Three weeks
>> ago, when set on equalize, the maximum voltage reading was 30.7, with
>> maximum amps of 46; this was reached around noon, and by around  
>> 1:30 pm
>> voltage/amps began its typical afternoon drop-off.  I attempted  
>> equalizing
>> on two other occasions since then--the last time this past  
>> Saturday, with
>> clear skies up until mid-afternoon--but having the same results.   
>> So, the
>> question is: are my batteries beginning their decline? We've had  
>> this set
>> for 4 1/2 years, so it would seem a bit too early for this, given  
>> that these
>> batteries are expected to last 7-10 years.
>>
>>
>>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> RE-wrenches at lists.re-wrenches.org
>
> http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> RE-wrenches at lists.re-wrenches.org
>
> http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20080802/1a0d0926/attachment-0003.html>


More information about the RE-wrenches mailing list