Hi Drake,
do you know how this is all done in say Germany?
I realize they have different codes ( hopefully) but how do they
address the main issue of potential bussbar overloading?
thanks,
jay
peltz power
On Jul 30, 2008, at 10:24 AM, Drake Chamberlin wrote:
> Thanks to All who have replied,
>
> First, to answer William's question
>
> "What is a "feed-through" breaker box and what are "feed-through"
> lugs?"
>
> A feed through panel is the type of service equipment often
> installed on pre-manufactured homes, where a main switch is needed
> outside the building, and a limited number of loads, fed from the
> outside, are also supplied. On the bottom of the busbar, there
> are lugs equivalent to the lugs for the service entrance cables.
>
> This is useful when feeder is to be installed to supply the breaker
> panel in the premise that is equal to the total service amperage.
> No breaker is needed for the run to the subpanel inside, since the
> wiring will be equivalent to the service cable. It is similar in
> function to a disconnect switch, but will typically have 4 to 8
> breaker spaces.
>
> The situation in this project is that a feed through panel is in a
> separate building from the building to be supplied from that
> panel. The building this panel is in has a separate electrical
> service, which is commercial. The service for the residence comes
> in through a separate meter, located on this same commercial
> building, then goes to the feed through panel. This panel was
> installed for us, for the sole purpose of allowing a feed from the
> solar array.
>
> The issue here is that the busbar will have 200 amps from the main,
> and over 40 amps from the solar. No power is to be taken from the
> residential service to feed the commercial building. There is no
> possibility of an overload on the busbar because the house has a
> main 200 A breaker that will limit the load from the panel.
>
> It could be argued that since the line to the house will have up to
> 240 amps available on a 200 amp service, that is too much. I would
> argue that a standard service drop can supply 10,000 amps
> instantaneously.
>
> The box is strictly to be used as an AC combiner and feed for two
> inverters. By the letter of the NEC, it does not seem to be code.
> I'm going to use Kent's suggestion and use a label, after running
> it by the AHJ beforehand.
>
>
> -Drake
>
>