XW6048 running a 1HP pump? [RE-wrenches]
    Mark Edmunds 
    mark.edmunds at xantrex.com
       
    Mon Jun  9 15:57:43 PDT 2008
    
    
  
Hi Scott,
The XW6048 will put out about 55Arms from line to line, or up to about
110Arms line to neutral (120V) for up to 15 seconds before hitting an
overload fault - this should be able to start a 1HP pump like this OK.
We have tested surge capability on several large motors, but would be
interested in hearing if anyone has got some real world results on
larger pumps so we know for sure!
The output current surge capability curves are in the XW operation guide
now, you can download at:
http://www.xantrex.com/web/id/1871/docserve.aspx
Cheers,
Mark
Mark Edmunds
Xantrex Technology Inc.
-----Original Message-----
From: Scott Carlson [mailto:scott at carlsonsolar.com] 
Sent: Monday, June 09, 2008 11:58 AM
To: RE-wrenches at topica.com
Subject: RE: XW6048 running a 1HP pump? [RE-wrenches]
My understanding is that the spinning flywheel mass on the generators
help
with the starting surges and I do not get a very clear response from
Xantrex
as to max amps when the inverter will protect itself and error out. The
breakers can handle the surges with quite a bit left over. By the way,
we
have installed a dozen XW's and love the new design, but have had
software
problems with the gsm's.
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
    
    
More information about the RE-wrenches
mailing list