XW generator start question [RE-wrenches]

Mark Edmunds mark.edmunds at xantrex.com
Fri Apr 25 08:57:25 PDT 2008


Hi Dan, Jay 


You have the correct information Dan - the original design did need the
"run" signal, even with 2 wire units - the software upgrade we now have
will allow the system to look at the AC2 voltage to determine that the
generator is running so it can be a true 2 wire installation.

Cheers,

Mark



Mark Edmunds
Xantrex Technology Inc.


-----Original Message-----
From: Dan Rice [mailto:danrice at scinternet.net] 
Sent: Friday, April 25, 2008 12:08 AM
To: RE-wrenches at topica.com
Subject: Re: XW generator start question [RE-wrenches]


Jay,

Yes, the GSM is required to interface a generator to the XW, 2-wire
start or otherwise. The GSM also requires a "generator running" signal
in order to recognize a running generator and hold the 2-wire signal
"on". The GSM "run"
sensor circuit requires a 12 volt nominal (30 volts max) signal from the
generator, and requires another 2 wires between the generator and the
GSM, so for a "2-wire" start generator, actually 4 wires are required.
Xantrex has heard the complaints about this loss of a true 2-wire start
feature on the XW, and I understand that there's a software upgrade
available that will allow the GSM to recognize when there's AC line
voltage present at the AC input terminals of the inverter (AC 2 in, I
assume). This should eliminate the need for the 12 volt "run" signal
(and the extra 2 wires) from the generator to the GSM. I haven't tried
this upgrade myself. On the one installation I've worked on, I ran the
additional 2 wires, and piggy-backed off of one of the propane solenoids
for the 12 volt "run" signal. The GSM works fine this way.

I hope that helps.

Dan Rice
Abundant Sun, LLC.

----- Original Message -----
From: "Jay Peltz, Peltz Power" <jay at asis.com>
To: <RE-wrenches at topica.com>
Sent: Thursday, April 24, 2008 7:20 PM
Subject: XW generator start question [RE-wrenches]


|
| HI All,
|
| Do you need the generator start module to control a 2 wire start
| generator on the XW inverter?
|
| thanks,
| jay
|
| peltz power
|



- - - -


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------







More information about the RE-wrenches mailing list