Bill,

Your response is somewhat promising to hear.  We have had three PV installations fall under the requirement of needing reverse power relays here in NYC.  At the end of the day, the equipment, design, installation, and third party witness testing averages about $20,000 in added cost to a project.  It's a very real concern that we will be severely limited on potential PV installations in our own backyard.  

If the utility is confirming that their network protectors shouldn't have much of a problem with anything less than enormous amounts of PV connected to their grid, then I wonder why they continue to show such concern over the 50kW and less systems that have been interconnected so far.  Do you feel that the IEEE workgroup is leaning in a more favorable direction toward PV?  I haven't gotten the same impression from a contact of mine who is part of that workgroup.



David


--
David Buckner
President

Solar Energy Systems, LLC.
1205 Manhattan Avenue
Suite 1210
Brooklyn, NY 11222-1058

ph 718-389-1545 (ext 11)
fx  718-389-2820
e  dbuckner at solaresystems.com




-----Original Message-----
From: Bill Brooks [mailto:bill at brooksolar.com] 
Sent: Monday, March 24, 2008 1:41 PM
To: RE-wrenches at topica.com
Subject: RE: Grid Tied PV on Area Networks [RE-wrenches]


Chris,

Mass. Utilities actually convened an IEEE workgroup on this subject. It is
ridiculous to say that small, inverter-based PV systems have any affect on a
secondary network, since, by definition, secondary networks handle many
megawatts of power. The network protector issue always comes up as the
reason, but I believe it is a red herring. The issue is not having too much
generation within a network so that there is always a minimum load flowing
through the protectors. You need an interconnection specialist help you with
this utility or you will not be installing anything within these networks.

I was in a meeting with the utility that has more secondary network
customers than anyone in the country two weeks ago and their engineers
agreed that it would take an enormous amount of PV before they would have a
problem with network protectors.

There are folks out there that can help--contact me off list.

Bill.


Bill Brooks, PE
Brooks Engineering
873 Kells Circle
Vacaville, CA 95688
office and mobile: (707) 332-0761
fax: (707) 451-7739
email: bill at brooksolar.com
web: www.brooksolar.com

Ecclesiastes 11:7 Truly the light is sweet, And it is pleasant for the eyes
to behold the sun

 

-----Original Message-----
From: Chris Anderson [mailto:canderson at borregosolar.com] 
Sent: Sunday, March 23, 2008 5:47 PM
To: RE-wrenches at topica.com
Subject: Grid Tied PV on Area Networks [RE-wrenches]



 

Wrenches,
 
We have run into an issue integrating grid-connected solar in some of
the older districts of Mass that have electricity grids comprised of
"area" networks as opposed to spot or radial networks.  It seems that
this type of network is not acceptable for interconnecting distributed
generation systems.  The issue appears to be the high level of
redundancy in the network as this type of grid is reminiscent of a peer
to peer computer network with individual electric consumers actually
being linked to one another.  
 
According to the Mass Tech Collaborative:
 
"An area network system typically serves a broader group of customers
located in a high-density area 
(such as a group of city blocks). Area network systems differ from spot
network systems in that they 
not only have multiple lines, transformers, and building connections but
also interconnections between 
the buildings. This means that power is flowing through even more paths
and in many different directions."
 
"...because area network systems allow power to flow through multiple
paths, adding a distributed generation 
generator to these systems introduces the risk of sending power into the
grid when the grid is not delivering 
power to the site, due to maintenance or system failures. This presents
significant risks to the safety of utility 
workers, performance of the distribution system equipment, and power
quality of other customers on the 
same network. Because of these risks, utilities must evaluate proposed
distributed generation on these systems 
more exhaustively than they do for radial interconnections."
 
In a technical bulletin on the MTC's webpage it states that:
 
"Area networks are designed to provide electric service that has a high
level of reliability and are more 
commonly found in urban territories.  By adding distributed generation
to an area network there is a 
possibility for reverse power flow through a network protector. [1]
This situation could adversely impact 
the safety of utility personnel, result in damage to utility equipment
and cause electricity fluctuations 
within the area network.[2]"
 
 
N-star (the utility) will apparently send us a letter with our
interconnection options. These may include: 
-Transferring your site's load from an area network to a radial
distribution system and interconnecting the generator on this system.
(not possible - this is an area network)
-Interconnecting the generator to a nearby radial distribution system
(again not possible given the lack of a radial dist system)
-Operating the load to be served by the generator off the grid (not
possible if we are to get a rebate for our clients)
 
 
So, does anyone have any experience actually installing solar on an area
network?
If not, does anyone have any thoughts on how we might?  
 
One thought might be to install some sort of current preventing diode
that would allow the system to be grid interconnected for the
grid-reference but prevent current from ever feeding the grid. Does
anyone know if this product even exists?
 
Thanks in advance!
 
Here are some further links about this:
 
http://masstech.org/cleanenergy/energy/glossaryelectricent.htm
http://masstech.org/cleanenergy/howto/interconnection/network.htm

 

 

 

Chris Anderson

Borrego Solar Systems, Inc.

 


[Non-text portions of this message have been removed]


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------








More information about the RE-wrenches mailing list