Why I abuse batteries was: trojan battery cycle [RE-wrenches]
John Berdner
jberdner at sma-america.com
Thu Feb 14 14:59:30 PST 2008
Jay:
The Sunny Island does do this to a large extent.
There is a daily charge profile, a longer (14 days) charge profile, and
a equalization profile (default 90 days).
These can be adjusted independently (votlage and time) and you can
schedule when charge cycles start using a timer function.
There is also a gen start based on load function that can be used to
run the generator when loads are highest.
All of this is over ridden if the battery state of charge falls too
low.
In a well designed system this normally does not occur but it will
start a generator and charge cycle if the batteries get too low.
Can you please elaborate a bit on your comment re: the efficiency of
the generator/charger ?
Best Regards,
John Berdner
>>> jay at asis.com 2/14/2008 09:02:59 AM >>>
Hi All,
I think this shows the need for what I have wanted for a long time,
A smart charger/inverter generator interface.
What I mean is one that you can program to battery charge to
different "levels" with adjustable intervals.
So you could do 10 cycles( adjustable) charging up to 80%, then
every 11th, it will EQ the batteries.
( or some variation of this)
Also a adjustable timer so that instead of turning on at 2pm, it will
wait until 6pm when the loads are really on. (fuzzy logic)
This is the next big advancement for those folks building inverter/
chargers to really improve the efficiency of the generator/charger.
Sure all this can be done with a smart owner operating the system,
but more and more of these systems are being run on auto we need
smarter charger programs.
thanks for listening,
jay
peltz power
--
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list