M-C branch plugs: Legal? Safe? [RE-wrenches]
Mick Abraham
mick at abrahamsolar.com
Mon Feb 4 17:19:35 PST 2008
Thanks to all who have replied...very helpful...
John Berdner: Thanks for reminding me about grid-tie situations where PV
string fuses are not needed. My present application is a battery based
system where I must consider possible backfeed from the battery.
"Ray Walters wrote: "...you can't use those connectors to create more
than 2 parallel strings, so I'm not sure how you would parallel 3
strings."
Mick says: On page 13 of the M-C catalogs for SolarLine 1 and SolarLine
2, they show trios plugged together in parallel. The M-C drawing looks
nice but one must wonder if plugged trios are really workable in the
real world, because that would need a PV module where the series fuse
rating is almost four times greater than the short circuit amperage.
Ray's mention that the Solar World 165s have a series fuse rating of 15
amps is most interesting, since their short circuit amperage is a much
lower 5.1. With the fuse rating so high relative to its amperage, this
module seems especially well suited to plug-parallel...in pairs at
least.
Thanks again,
Mick Abraham, Proprietor
www.abrahamsolar.com
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list