Mark:
Interesting commentary. Thanks for your input.
Regarding 690.33 E today: This problem is not with a future code version,
it is a problem with current code version (2002 at least). If so, ALL
installations happening in the US as of today are in violation. Is this
your understanding?
Regarding 690.33 E in 2008: There are new restrictions proposed in 2008
that require conduit protection of PV wire accessible to the public. Is
this your interpretation?
Regarding European applications: Ground fault protection will not prevent
arcing across connectors opening under load until ground fault diversion is
reached. In US inverters, the ground fault detection is typically 1 amp
and will not open until some time delay has occurred. The ground fault
protection in modern inverters is more aptly named ground fault detection
and is designed to shout down inverters and prevent fires, not protect
personnel. The ground fault currents in a US Inverter system are
definitely fatal.
William Miller
At 03:22 PM 1/22/2008, you wrote:
>The whole thing about the MC connector and why we are also in trouble with
>690.33 is that the MC is not rated for opening under load. This means that
>ALL connectors regardless of location, guarding, fencing, etc. will have to
>be locking (until they can shrink a Square D HR331 down to the size of an MC
>connector) because they are not designed to open underload. Forget about
>the execption for locking connectors based on location.
>
>The no exposed metal is only part of a "dead front" design to make them safe
>to handle, during assembly.
>
>Once they are assembled, and current is running thru them it is a different
>story.
>
>So what does happen if they are pulled apart while under load? Low
>current-low voltage, high current-high volatage"
>
>Two issues arise, 1- potential injury to operator due to DC arc, 2- damage
>to connector such that it cannot be re-made.
>
>The reason there is no proble with accidental open in Europe is the whole
>system has GFCI grade protection, correct?
>
>All of this is separate from 690.31, if the "circuit" is readily accessible,
>the "conductor" SHALL be in a RACEWAY.
>
>MPF
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list