Fire Department. Regulations [RE-wrenches]
William Miller
wrmiller at charter.net
Thu May 15 21:37:37 PDT 2008
<x-flowed>
Friends:
I appreciate the valuable dialog here. This forum has been a wealth of
knowledge-- indispensable. I have learned a few things in the last 24
hours (some opinions expressed as well):
Venting: Letting the smoke out is only one function of cutting a hole in
the roof. If the fire is in the kitchen, they want to cut a hole right
over the kitchen and also dump water in. So if the kitchen is on the south
side of the house, cutting a hole in the north roof pitch is less effective.
Attics: If the purpose of cutting the hole were only for venting, cutting
a hole in the north pitch would help only if there was an attic connecting
all sections of the home. If any cathedral or vaulted ceilings exist, the
need is to cut multiple holes.
Standards: They are just now being developed. I really prefer the Cal
Fire setbacks. Losing the short edge of a roof is far less of an impact on
PV than losing the long edge. The Cal Fire standards allow you to install
right up to the lower eave and only require 3 foot clearance to the ridge
and gable eaves.
Quick disconnects: They are mentioned in the LA Fire Department standards
for both hardware and connectors but not really explained. They are not
mentioned in the Cal Fire. In San Luis Obispo, the fire marshal is willing
to let us install in the setback area if there is some means to quickly
remove or "flop over" rows of modules at a maximum of 4 modules per
move. This is a great precedent and one I hope we can encourage. This
means the industry can develop hardware to allow us to use the precious
roof space we need (and the customer needs). I encourage each of you to
promote this to your local fire marshal. I also encourage entrepreneurs to
develop hardware and connectors to allow us to install PV in the disputed
zones and still allow fire fighters to clear them from the roof with utmost
expediency. This is a market opportunity, folks.
PV modules starting fires/fire fighter safety: One poster here supposed
this was about PV systems starting fires. It is not. This is about
allowing fire fighters to do their dangerous work without further
impediments. Fire fighters should not be expected to walk on the slippery
surface of PV modules nor should they be expected to cut or break through
energized modules. Depending on which module you break, you might achieve
contact with up to 600 VDC.
Politics: In my opinion, we must avoid any perception that we do not care
about the safety of fire fighters. I tell my crew, "I'll give the money
back to my clients before I'll see one of you hurt on the job." We must
have the same empathy with fire fighters. With some negotiation and
technical advances, we can accommodate their needs and ours.
Roof top disconnects: Nowhere do I see any provisions to protect fire
fighters from cutting into conduits with high voltage DC. It seems to me
this is also a hazard. I hesitate to bring this up, but why not get this
all solved at once? I think that firefighters use demolition saws to cut
through roofs and these saws can cut through EMT like butter. My opinion:
The 200 5 NEC standard for metal conduit is almost enough. I would
add: No aluminum conduit and, conduits must not run under
rafters. Instead, conduits should leave roof surfaces at 90 degrees and
stay a minimum of 18" away from the underside of a roof.
Thanks again for all of your thoughts and support. I really think we can
get a good solution that may coast a few dollars more but will not reduce
system size.
William Miller
PS: LAFD and Cal Fire standards are now on our web
site: www.mpandc.com/resources/resources.html
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list