[RE-wrenches] offgrid system question

Phil Undercuffler P.Undercuffler at conergy.us
Tue Aug 19 07:39:55 PDT 2008


The XW6048 is rated at 52 amps RMS line to line between 5 seconds down
to 1 millisecond, so if your client's AC has a starting inrush surge of
104 amps at 240v, then yep, I think your biggest problem is not enough
inverter.  Sounds like just one additional inverter will be marginal;
depending upon the additional background loads you may want to consider
expanding to three total.  I think Mick Abraham is right on here, in his
earlier post.

 

Phil Undercuffler

Director, Battery-based and Off-grid

Conergy Sales & Systems, Americas

Our World Is Full of Energy

1730 Camino Carlos Rey Suite 103

Santa Fe, NM  87507

p.undercuffler at conergy.us <mailto:p.undercuffler at conergy.us> 

Direct | 505.216.3841

Toll Free | 888.396.6611 x4841

Fax | 505.473.3830

www.conergy.us <http://www.conergy.us/> 

________________________________

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Max
Balchowsky
Sent: Tuesday, August 19, 2008 6:45 AM
To: mick at abrahamsolar.com; RE-wrenches
Subject: Re: [RE-wrenches] offgrid system question

 

You're right Mick, It is an XW 6048, there's only one and I really think
I'm going to find that the biggest problem is that there is not enough
inverter capacity capacity with just one unit (the scematic shows a 60
amp breaker on the output). The system is new ( installed within the
last 4 months and the batteries were new) The AC unit is 240 volt.....

 

Max Balchowsky

SEE Systems





 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20080819/c09e34ef/attachment-0002.htm>


More information about the RE-wrenches mailing list