Drake:
Sorry again, but this is still not clear. Questions below in red (could
you draft a block diagram and post it?):
At 03:56 PM 7/30/2008, Drake Chamberlin wrote:
>>2. The commercial building has a service that you will not feed the
>>grid-tie to.
>
>Yes. It also has its own service. The commercial building gets some
>solar also. The tax benefits would be for it all to be on the commercial
>service, but we are following the owner's request.
According to the two paragraphs above, the commercial building has two
commercial services??? One will receive PV and one will not??
>>3. This commercial building has a "feed-through" breaker panel that was
>>installed for the PV to tie to. This "Feed-through" box does not connect
>>to the commercial service.
>
>Yes
>
>>Where is the service that the PV system would feed? In a separate building?
>
>Yes, in the residence on the property. The meter is on the commercial
>building.
Referring to the passage above: I have learned that in most cases, the
service and the meter are the same device. Are you telling me the legal
service is separate from the meter???
>>Where does the feeder connected to the bottom of this "Feed-through"
>>panel go?
>
>
>
>It goes to the residence, which is another building on the same property.