SMA Combi-Switch questions about UL rating [RE-wrenches]
Allan Sindelar
allan at positiveenergysolar.com
Wed Dec 12 18:15:30 PST 2007
----- Original Message -----
From: "Larry Crutcher, Starlight Solar" <larry at starlightsolar.com>
To: <RE-wrenches at topica.com>
Sent: Wednesday, December 12, 2007 6:33 PM
Subject: RE: SMA Combi-Switch questions about UL rating [RE-wrenches]
>
> Yes Steve, but the fact that UL HAS limited this switch to 11.5 amps for
> PV use must be considered. Just because SMA packages it does not
> invalidate the original UL restriction. I can't say it "sounded
> reasonable" to an inspector or insurance company or attorney or judge.
> You get the picture? There is a reason for the limitation.
>
> Are any wrenches using the HU361 for more than 11.5 amps of PV?
Yes, Steve, we are. Here is our logic:
According to the SMA spec sheet
(http://download.sma.de/smaprosa/dateien/4286/Combi-Switch_Flyer_081106.pdf)
,
the Combi-Switch is designed to match well with the SB6000 using four
strings. It is rated for up to 40A, with 4 10A Touch-safe fuseholders. So we
have used it with four strings of ten 160-170W 24V modules.
I think the key is that SMA has had their product, the Combi-Switch, listed
by ETL (not UL) to UL1741. Bingo, end of story, install according to the
manufacturer's instructions. The fact that it's based on an HU361 is
irrelevant; it's now a separate listed product.
At least, that's how we have seen it. Could be wrong, though...
Allan @+E
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list