Hi Dick,
If you got shocked on a neutral, I'm guessing that there was a
problem in the circuit. It is pretty hard to get a shock from less
than 12 volts. If you have a 5% voltage drop on a 120 volt circuit,
you have 6 volts to ground. I've licked my fingers and put one on
the positive and one on the negative of 24 volt battery banks, and
never felt a thing. I get a jingle from open circuit, 24 volt
nominal PV systems, which are usually near 40 VDC.
5% on a 600 volt circuit would be 30 volts to ground, which one could
feel if s/he were well grounded.
Drake
>BE CAREFUL! The shock you can get from touching a "fully connected neutral"
>could well be
>the one that kills you. If there is no current in it, and often this
>is hard to
>know, you would not get a shock. If there is current in it, you have presented
>that current with a parallel path to ground. If you don't get a shock you have
>only been very lucky.
>In that case, you were of sufficiently high resistance to avoid one.
>
>If you are sweaty, standing on concrete or earth, touching steel, etc.,
>(especially when dealing with higher voltages,
>although 120 volts kills more people than any other) you won't
>forget it .....
>if you survive. Been there done that.
>Dick Ratico
>Solarwind Electric
>Bradford, VT
>
>You wrote:
>"The only time you can get shocked from a neutral is when it is
>disconnected from the ground bus. A fully connected neutral should
>be safe even if current is running through it."
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: re-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list