PV Negative color [RE-wrenches]
Drake Chamberlin
Drake.Chamberlin at redwoodalliance.org
Fri Dec 7 09:24:56 PST 2007
<x-flowed>
At 08:22 PM 12/6/2007, you wrote:
>I think that a solidly grounded conductor should be
>white, or not, BUT when working with systems using a
>ground fault breaker or fuse and is therefor a fused
>grounded conductor, it should not be white. If a
>ground current makes the wire hot, don't call it
>grounded. If the only way it can become hot is when
>it is broken then it can be called grounded.
This sounds right. The negative wire can exist in junction
boxes, and if it is white and operating at high voltage DC due to
the normal operation of the ground fault device, it could pose a
serious hazard to electricians troubleshooting other systems.
The automotive and marine designations of black and red are
problematic, due to the fact that black is often positive in NEC
compliant wiring. Maybe yellow would be a good recommendation for
negative. The not-always-grounded negative wire on a PV ground fault
system is a unique, as far as I know.
A far better ground fault system would be one that opened the
conductors at the array, instead of at the end of the run, where a
ground fault could continue indefinitely. Control wires could be run
through the mandated metal conduit to the control center. A hot
neutral would not be a likelihood.
The 2008 code has new rule to limit the existence of hot, white wires
by requiring all multi wire branch circuits to open all conductors
simultaneously. That means that if you are working on a split 240
volt circuit or a 120/208 Volt 3 phase, all circuit conductors will
open with a 2 or 3 pole breaker, and it will be safe to disconnect
the neutral anywhere in the system. As this method becomes mandated,
the electricians are liable to feel too safe with white wires.
Drake
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: re-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list