Hi Drake,
For transfer switches, I often use 2 breakers next to each other with a
handle tie interlock. I have used them with Square D up to 70 amps and
Murray/Seimans/ITE up to 100 amps. I think GE has a handle tie interlock
for two breakers across from each other.
I like this method for manual transfer because it can be in the same panel
as the breakers for all of the backed up loads.
I have even done a few systems with the old style Murray 100A panels that
had the main breaker lined up with the right hand row of breakers instead of
centered where the 100A main breaker was interlocked with a 60 amp generator
just below it for a complete AC protection and transfer system in one box.
Ron Schroeder
WD8CDH
NABCEP Certified PV Installer
----- Original Message -----
From: --- Drake Chamberlin
> <Drake.Chamberlin at redwoodalliance.org> wrote:
>
>>
>> Does anyone know of a good source for a 60 amp, 240
>> volt contactor or
>> transfer switch? I need one for a Sunny Island,
>> grid backup system with
>> AC coupled Sunny Boys and a generator.
>>
>> Drake
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list