Inverter location [RE-wrenches]
Bill Brooks
bill at brooksolar.com
Wed Jul 11 14:25:51 PDT 2007
Marco,
You are correct. Inverter terminals are always higher voltage than the
service entrance voltage when there is current flowing out of the inverter.
The voltage drop is dropping from the inverter to the service entrance.
Example:
Service entrance voltage: 255Vac
Inverter to service entrance voltage drop: 3% at full power
Inverter terminal voltage: 262.6 Vac
Inverter trip voltage: 260 Vac (not the published value, but the actual
value that the inverter trips at to meet the 264 Vac standard)
In this example, the inverter has tripped offline and will continue to trip
offline until the power from the inverter decrease to 66% of full power
creating only 2% voltage drop rather the 3% at full power.
Bill.
Bill Brooks, PE
Brooks Engineering
873 Kells Circle
Vacaville, CA 95688
office and mobile phone: 707-332-0761
fax:707-451-7739
email: billbrooks7 at yahoo.com
web: www.brooksolar.com
Ecclesiastes 11:7 Light is sweet, and it pleases the eyes to see the sun.
> -----Original Message-----
> From: Marco Mangelsdorf [mailto:marco at pvthawaii.com]
> Sent: Wednesday, July 11, 2007 10:34 AM
> To: RE-wrenches at topica.com
> Subject: RE: Inverter location [RE-wrenches]
>
>
> Bill,
>
> Did you mean to say tripping of "because of high voltage at the inverter
> terminals," amigo? Seems to me, at least in these here parts, that a 3
> percent voltage drop usually means a lower voltage at the terminals, no?
>
> marco
>
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list