IF you did this, you would have to find coax with an insulation rating
as high as the AC voltage.
Todd
Nicholas Ponzio wrote:
>Is there a way to legally run AC inverter output through a conduit (2" PVC)
>that already has co-axial TV cable in it?
>
>My reading of the code (see below) suggests that we need a "permanent
>barrier or listed divider." What constitutes a divider?
>
>Thanks in advance for any suggestions or insights.
>
>
>
>* NEC Reference:
>800.113.A.1.5.c Communications conductors shall not be placed in any
>raceway, compartment, outlet box, junction box, or similar fitting with
>conductors of electric light, power, Class 1, non-power-limited fire alarm,
>or medium power network-powered broadband communications circuits.
>
>Exception No. 1: Where all of the conductors of electric light, power, Class
>1, non-power-limited fire alarm, and medium power network-powered broadband
>communications circuits are separated from all of the conductors of
>communications circuits by a permanent barrier or listed divider.
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list