Commercial line tap [RE-wrenches]
August Goers
august at luminalt.com
Wed Apr 11 08:46:04 PDT 2007
It is an underground service, as seen in the photo "C" below (see left hand
side of panel). I'm new to this, so it is very possible that I am missing
something. However, the top of the panel is above the meter on the utility
side. We need to tap in after the meter otherwise we're going to send the
utility non-metered free energy. As Jeff O mentioned, I think we need to tie
in somewhere behind the red arc shield above the main 400 A breaker. I'm
going to head out there next week to see if there are any provisions behind
that read arc shield. -August
http://www.luminalt.com/temp/400AMainA.JPG
http://www.luminalt.com/temp/400AMainB.JPG
http://www.luminalt.com/temp/400AMainC.JPG
Wrenches:
I am planning a ~26 kW commercial PV system which will be tying into a 3
phase 208 V service. I am new to these commercial 3 phase systems so I'm
seeking some help and design ideas for tying into the service. The 400 A
main service panel is maxed out with a 400 A main breaker so we won't be
able to tie our 200 A solar breaker in on the load side. I suppose we're
looking at either a line tap or a service upgrade to a 600 A main. Space is
extremely limited around the main panel - there is not a good area to place
an external fused disconnect so we're hoping that we can fit something in
within the main panel.
The attached photo shows the main panel partially opened up. Any information
on the best way to perform a line tap would be appreciated. Other ideas are
welcome. I'm trying to get some help from Square D but haven't had any luck
yet.
Thanks in advance,
August Goers
Managing Engineer
Luminalt Energy Corporation
Office: (415) 564-7652
Mobile: (415) 559-1525
www.luminalt.com
august at luminalt.com
-----Original Message-----
From: Steve Johnson [mailto:stevejohnson at comcast.net]
Sent: Tuesday, April 10, 2007 7:58 PM
To: RE-wrenches at topica.com
Subject: RE: Commercial line tap [RE-wrenches]
I must be missing something here. Isn't that your feeder at the top with
a spare lug on each phase? Can't you tap in there with your 200 amp
feeder to the PV distribution panel?
What does the outside look like? Overhead or underground?
Steve Johnson
LightWave Solar Electric
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
[Non-text portions of this message have been removed]
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list