We always used the rule of thumb from the Ananda power centers, Trace,
etc.: 2/0 cable gets a 200A T fuse or 175 A breaker, 4/0 gets a 400A T
fuse or a 250 amp breaker. If you look at the trip curves it makes more
sense. TheT fuses definitely trip faster (lower current) than the Heinemans.
I ordered some 300 A fuses once through Summit Electric they were over
$50 a pop. I quit looking at the in between sizes after, and all has
been well since.
Ray
Allan Sindelar wrote:
>Wrenches,
>What is a good wholesale source for 225A or 250A Class T fuses, of the
>bolt-on type that has been used in our industry for years? Readily-available
>sizes through PV distributors have always left a gap between 200A and 300A
>sizes. I need two only. Thank you.
>