PV Negative color [RE-wrenches]
Mark Frye
markf at berkeleysolar.com
Mon Dec 10 10:14:18 PST 2007
OK, Thanks Ray. I missed that. The call out is still smaller than #6,
not #4, but your point is well taken and much appreciated.
Interesting stuff. So as long as you use USE-2/RHW-2 or similar all the
way thru from module to inverter, you can mark #6 or smaller, but if you
transition to THHN or similar, in a box on the roof for instance, the #6
or smaller has to be factory colored.
R. Walters wrote:
>
>
> RIght on the same page, man.
> 200.6 (A) #2 allows PV system conductors #6 and smaller to be taped.
>
>
> Ray
> On Dec 6, 2007, at 7:40 PM, Mark Frye wrote:
>
> >
> > Ray, I am not sure where you are getting this?
> >
> > According to Article 200.6 (B) only wires #6 or larger can be
> > identified
> > "(3) At the time of installation, by a distinctive white or gray
> > marking
> > at its termination....."
> >
> > What am I missing?
> >
> >
> > R. Walters wrote:
> >>
> >>
> >> Code allows us
> >> to tape PV wires smaller than #4.
> >
> >
> > - - - -
> > Hosted by Home Power magazine
> >
> > To send a message: RE-wrenches at topica.com
> >
> > Archive of previous messages: http://lists.topica.com/lists/RE-
> > wrenches/read
> >
> > List rules & how to change your email address: www.mrsharkey.com/
> > wrenches/etiquette.php
> >
> > Check out participant bios: www.mrsharkey.com/wrenches/
> >
> > Moderator: michael.welch at homepower.com
> >
>
> R. Walters
> Solarray.com
> NABCEP # 04170442
>
>
>
>
> --
> [Non-text portions of this message have been removed]
>
Berkeley Solar Electric Systems
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list