Geof,
I'm budgeting a system like this too, but with a 500 kw diesel genset
(proposed by others). This genset would be transfer switched to another
system backed up with a 225 kw diesel which is in tandem with some
inverters with batteries and some grid-tied and AC coupled with PV.
Maybe 60 kw PV.
When the 225 diesel generator is on it would run close to full bore, say
80% or so, charging batteries and running the grid. When batteries get
charged it shuts off.
The grid tied PV and battery/inverter systems would operate the system
quietly as long as capable. When batteries get to 50% the 225 diesel
kicks in and supplies grid while charging batteries, then shuts off
again. This is just a preliminary design and no I haven't done a
successful (or unsuccessful) project like this before.
The battery inverters would have to set the "tone" for the grid as they
are the only thing always available. But if they set the grid standard
then how can the genset match it? This is where I am stuck. But then it
is late . . .
Steve Johnson
LightWave Solar Electric
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list