208 V 2 pole meter solution [RE-wrenches]
Steve Johnson
stevejohnson at comcast.net
Thu Dec 27 09:31:38 PST 2007
Well, the solution, in this case is to add a "5th terminal" this is a
lug that gets added to the meter and allows a "form 12s network meter"
to read 2 phases of a 3 phase service. At least thats what I am told by
local meter dept. I may now check my other installation (which is out
of town) against the inverter kwh and see if they are close. I think
the form 2s meter might read low if there is a problem.
google books link
http://books.google.com/books?id=c0EzRqhRrmsC&pg=PA50&lpg=PA50&dq=12s+network+meter&source=web&ots=w2bYhbBzn2&sig=yv6mrgRWuZqfkFNJqIwpFGapErw#PPA50,M1
An Account Reviewers Guide to Electric Meter Troubleshooting
By Virgil Johnson
http://www.csu.org/extrx/util_dev_svcs/svc_standards/electric/chapter/appendix_e.pdf
page 4.
Jeff and Darryl say their installations are tracking the inverter kwh
reading ok, so I don't know what it all means. The 5th terminal is a
$6 add on and makes the local meter dept happy so I'll keep the local
peace.
Steve
jeff wrote:
>
> I concur with Darryl. We've used several CL200 240V 3W (single phase)
> glass
> bulb meters connected line to line on 208Y120 three phase service and
> they
> work just fine, meaning that over time the meter reading and inverter
> E-total are within a few percent of each other.
>
> If you have doubts or need meter help, Austin International in SC is
> pretty
> helpful.
>
> Jeff Irish
> Hudson Valley Clean Energy
>
> -----Original Message-----
> From: Darryl Thayer [mailto:daryl_solar at yahoo.com]
> Sent: Tuesday, December 11, 2007 5:26 PM
> To: RE-wrenches at topica.com
> Subject: Re: 208 V 2 pole meter [RE-wrenches]
>
>
> I am surprized if he is correct. The meters work on
> 120 to 240 volt just fine, your power is single phase
> added to a three phase load, your meter is single
> phase, I think it will work. Perhaps you can get
> intouch with the meter people.
> Darryl
> --- Steve Johnson <stevejohnson at comcast.net> wrote:
>
> >
> > I have installed a SB 400US in a system with a PV
> > production meter. The
> > main meter is a 208v, 3 phase CT. The PV production
> > meter is on the
> > load side of the main meter. From the inverter it
> > goes through an AC
> > disconnect, through a 2 pole feed through meter
> > base, and onto a 2 pole
> > breaker in the main panel.
> >
> > The utility meter guy says his 2 pole 240 v
> > single(split) phase meter
> > won't read the 208v 2 pole output of the Sunny Boy
> > correctly because it
> > has a 240 volt coil in it. Says they don't make a 2
> > pole 208 volt
> > meter.
> >
> > Is this right? What to do? I guess I could change
> > the meter out to a 3
> > phase 208v meter base and they could put in a feed
> > through 3 phase
> > meter, there just wouldn't be any power on the third
> > leg.
> >
> > Anybody else run into this?
> >
> > Steve
> >
> > Steve Johnson
> >
> >
> > - - - -
> > Hosted by Home Power magazine
> >
> > To send a message: RE-wrenches at topica.com
> >
> > Archive of previous messages:
> > http://lists.topica.com/lists/RE-wrenches/read
> >
> > List rules & how to change your email address:
> > www.mrsharkey.com/wrenches/etiquette.php
> >
> > Check out participant bios:
> > www.mrsharkey.com/wrenches/
> >
> > Moderator: michael.welch at homepower.com
> >
> >
> >
>
>
>
>
> ____________________________________________________________________________
>
> ________
> Be a better friend, newshound, and
> know-it-all with Yahoo! Mobile. Try it now.
> http://mobile.yahoo.com/;_ylt=Ahu06i62sR8HDtDypao8Wcj9tAcJ
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
>
Steve Johnson
LightWave Solar Electric
Nashville, Tennessee
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list