Xantrex MPPT60-150 Calcs [RE-wrenches]
William Miller
wrmiller at charter.net
Mon Dec 10 17:47:39 PST 2007
<x-flowed>
Friends:
I am hoping our Xantrex Rep or knowledgeable colleague can verify my
calculations on a Xantrex charge controller system. The modules used will
be Solar World SW175 mono:
Regarding voltage: The MPPT60-150 has an open circuit voltage maximum of
150 VDC. I must limit my strings to 2 modules because: With 44.4 VOC per
module, times 3, times the NEC Correction factor of 1.13 in our climate,
exceeds 150 VDC by 0.516 VDC. So string quantity is 2, maximum. Correct?
Regarding amps: Rated amps (MPP) per module is 4.95. If I use 10 strings,
rated amps is 49.5. 690.8(A)(1) requires I multiply by 125%. The answer
is 61.875, or, in excess of the charge controller's rating. Therefore my
limit is 18 modules or 9 strings.
What comes to mind is that certain calculations require a 125% for
continuous duty on top of another 125% calculation for solar applications
(edge of cloud and all that). I recall a conversation with Outback tech
support some time ago and they claim the MX-60 is rated for continuous duty
and therefore at least one of the 125% de-ratings is not necessary. I
assume this is true also for the Xantrex charge controller?????
However, I must still meet the requirements of 690.8(A)(1) and use one of
the 1.25 multipliers. Therefore I am limited to 9 strings, or 18 SW175
modules.
How does SC current work into charge control design? I see no reference in
690(A)(1) to Short Circuit current.
The claim that a charge controller is assumed to be rated to operate as a
continuous duty device is supported by the exception in this
section: Exception: Circuits containing an assembly, together with its
overcurrent device(s), that is listed for continuous operation at 100
percent of its rating shall be permitted to be utilized at 100 percent of
its rating. How about the circuit breakers in the Xantrex "Chassis
distribution Channel?" Are these considered to be part of the assembly, or
are standard 60 amp circuit breakers not adequate?
Thanks to Xantrex and any others who can check my math and my application
of the NEC. This calculation applies also to Outback MX-60 charge
controllers so I appreciate any input form Outback.
William Miller
-- _________________________________
William Miller
Miller Power and Communications
Voice :805-438-5600 Fax: 805-438-4607
email: wrmiller at mpandc.com
http://mpandc.com
License No. C-10-773985
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list